The two units use the same battery. So, a unit with a higher allowable VA rating will have a shorter runtime. The 9AH battery is the limiting factor.here is something puzzling to me. On CyberPower's site, they list the CP1350AVRLCD3 as running for 14/4min on half/full load. but they have the CP1500AVRLCD3 running for 12/3min on half/full load. why would that be? could it be a misprint?
My APC commercial 1500VA UPS uses four 12V 9AH batteries. Still 1500VA but four times the battery reserve. You can't use the VA rating to judge a UPS.