HELP ! if my is power supply 1200 watts should i buy 1200 watts UPS ??

Page 2 - Seeking answers? Join the Tom's Hardware community: where nearly two million members share solutions and discuss the latest tech.
Status
Not open for further replies.

settlementmen

Distinguished
Jul 27, 2013
121
0
18,680
hey guys i need a UPS for my Workstation PC it has a 1200 watts power supply, i always use on a full load for 3d rendering in 2k resolution, i have a dual Cpu motherboard. I really need UPS for my PC , and for my professional works , so my question is, if i have 1200 watts power supply should i buy 1200 watts UPS ? or i can by any UPS ?? PLEASE ANSWER thanks !!!
 
Solution
You have to understand that a 1200W PSU draws only as much as required. If your system requires 200W at idle and your PSU is 80% efficient, then it will draw (200/80 * 100) which is 250W. If your batteries are 4-5 years old, then I'd be surprised if the UPS passes the battery test. Instead of conecting your system, connect something else like a 100W light bulb and see if the UPS stays powered up for at least an hour. I have a Smart-UPS 1000 and a Smart-UPS 1500 and they can run for at least 1/2 hour when my systems are idle (except the 1500 that shutdown within a couple seconds when there was a power outage and the batteries were at least 3-4 years old, but that's normal). You can buy 8A batteries, but you probably won't find 14A...
A CRITICAL item most people don't even know about, is that many UPS units will NOT work with a PSU that provides ACTIVE Power Factor Correction (PFC), yet the same UPS works 100% OK with same or even much higher wattage NON-active Power Factor Correction PSUs.

Unfortunately, the specs provided on many retail sites and even on a manufacturer's product page do NOT indicate whether or not the UPS supports active PFC. Some do...some don't.

Bottom line: make sure the UPS you buy supports the type of PFC your power supply uses.

You may have to dig into the DETAILED specifications and in some cases even have to email or call the manufacturer to find out whether the UPS supports power supplies with Active PFC or only supports power supplies with NON-active PFC.

For example, I have a Corsair 750W PSU that has Active PFC which, at the time of purchase, "Active PFC only" was not spec'd on the UPS retail product page. But, my (never having failed before) 900Watt capable UPS FAILS and shuts down after an AC mains power failure when it tries to continue supplying power to that 750W Active-PFC power supply . This happens even though the running system was consumiing less than 200Watts (confirmed by two different hardware meters from different manufacturers)...yet, that same UPS RELIABLY powers different NON-active PFC PSU's running at about 500Watts (PF~.8) on different systems, or when tested by simply running six 100W incandescent bulbs (600Watts total and incandescent bulbs PF~1).


Added note: In addition, make sure the type of UPS output (sine-wave, simulated sine-wave, square-wave, etc) is compatible with your intended load/system
 