Question New PSU makes UPS click on startup - - - is it overloaded ?

May 14, 2024
8
1
15
I just got an ASRock PG-1300G PSU for my 5090 GPU. I ran it at full load with Furmark for 10 minutes and played Helldivers 2, everything seemed fine. But I notice that when I press the power button to turn the PC on (when it's totally off), my UPS clicks and the display lights up almost like it was momentarily overloaded. Is that odd? My previous power supply didn't do that and I'm not sure what to make of it.
The UPS has a max load of 900W
 
My previous power supply didn't do that and I'm not sure what to make of it. The UPS has a max load of 900W
Make and model of your UPS and it's age? Make and model of your PSUY prior to the ASRock PG-1300G?

Moved thread from Components section to Power Supplies section.
 
when I press the power button to turn the PC on (when it's totally off), my UPS clicks and the display lights up almost like it was momentarily overloaded. Is that odd?
Not really. Quite a few ATX PSUs momentarily draw up to 100A from the AC mains at initial switch on, especially from a nominal 230V 50Hz supply. Even from a nominal 115V 60Hz mains supply, the switch-on surge can be tens of Amps.

With a large PSU like the PG-1300G rated at 1300W, it's possible the switch on surge is too much for your old 900W UPS.

By the way, what is the VA rating of your UPS? I'd expect it to be roughly 1500VA if it has a 900W output, as per this APC unit:

https://www.se.com/uk/en/product/SM...usb-and-serial-communication-avr-graphic-lcd/
 
Not really. Quite a few ATX PSUs momentarily draw up to 100A from the AC mains at initial switch on, especially from a nominal 230V 50Hz supply. Even from a nominal 115V 60Hz mains supply, the switch-on surge can be tens of Amps.

With a large PSU like the PG-1300G rated at 1300W, it's possible the switch on surge is too much for your old 900W UPS.

By the way, what is the VA rating of your UPS? I'd expect it to be roughly 1500VA if it has a 900W output, as per this APC unit:

https://www.se.com/uk/en/product/SM...usb-and-serial-communication-avr-graphic-lcd/
It's this model: https://www.apc.com/us/en/product/B...bcategory-id=88975&selectedNodeId=27590292604

Interestingly, it hasn't been doing it now. Everything starts up normally. But from what I can tell 900W is as high as you can go with UPSs unless you want to spend huge amounts on units with loud fans that run constantly
 
Not really. Quite a few ATX PSUs momentarily draw up to 100A from the AC mains at initial switch on, especially from a nominal 230V 50Hz supply. Even from a nominal 115V 60Hz mains supply, the switch-on surge can be tens of Amps.

With a large PSU like the PG-1300G rated at 1300W, it's possible the switch on surge is too much for your old 900W UPS.

By the way, what is the VA rating of your UPS? I'd expect it to be roughly 1500VA if it has a 900W output, as per this APC unit:

https://www.se.com/uk/en/product/SM...usb-and-serial-communication-avr-graphic-lcd/
Nevermind it just did it again lol

It seems to happen randomly but there must be some trend. It makes the UPS switch from outlet power to battery power just for a moment. I'll also note that the lights sort of flicker


I live in a brand new house so the electrical system should be fine to handle this much
 
"It makes the UPS switch from outlet power to battery power just for a moment. I'll also note that the lights sort of flicker"

Not surprising the room lights sometimes flicker. Some ATX PSUs momentarily pull a very high current out of the wall socket (and through your UPS) at switch on.

Some PSUs are worse than others. I couldn't find current surge figures for your 1300W unit, but here is a cheap 550W PSU that pulls a hefty 86.31A from a 230V AC input (my mains is 240V). The switch on surge is usually lower for 115V AC supplies, but can still be quite large. With any luck, your Asrock PSU will have a better designed inrush current limiter.

https://www.tomshardware.com/reviews/xpg-pylon-550w-power-supply-review/2

Inrush current, or switch-on surge, refers to the maximum, instantaneous input current drawn by an electrical device when it is first turned on. A large enough inrush current can cause circuit breakers and fuses to trip. It can also damage switches, relays, and bridge rectifiers. As a result, the lower the inrush current a PSU has right as you turn it on, the better.

tuAZnsi48c3t9zx6iyCjs9-1200-80.png.webp



It's good to see your APC UPS is rated at 1500VA/900W. I doubt you'll ever exceed 900W unless you hang several more computers on the system. However, you do have a "brute" of a PSU and it obviously affects the operation of your UPS.

I have a similar APC UPS also rated at 1500VA, but it's physically bigger than your unit and probably a different design. The link below is for the 120V version, but mine is the 230V version. I think the main difference is mine holds two 12V batteries, not one.

https://www.amazon.com/APC-SmartConnect-Interactive-Uninterruptible-SMC1500C/dp/B077Y62GSJ

51dyj-6pblL._AC_SL1280_.jpg



I had three PCs and monitors running on it yesterday, plus two hardware firewalls and a bunch of network switches. None of them were consuming huge amounts of power, but I don't see any flickering lights when switching on systems.

It may just be that your 1300W PSU would be happier on a 2200VA or 3000VA UPS as regards switch on surge. I'm not suggesting you should go out and buy a 2200W UPS though.
https://www.amazon.com/APC-Smart-UPS-SmartConnect-Uninterruptible-SMT2200C/dp/B077YDWR3Y

Just be aware that high switch on currents can eventually burn out electrical contacts in mains switches and mains relays. I've replaced various switched mains outlet sockets and relays over the years (in series with ATX PSUs) and discovered melted and blackened contacts inside. It can take years before things fail but cheap switches/relays go sooner than quality products.