BUlly_boy_2101 :
i do not think the psu is faulty because i just bought it yesterday!!!
You bought a RM650 yesterday, new doesn't mean working properly.
1. A certain % of power supplies are delivered DOA or with faults that warrant an RMA. In the past 6 month study period 1.55% of all Corsair PSU's were replaced under warranty
2. The RM series does not have very good build quality with a BQ rating of 7.0
http://www.jonnyguru.com/modules.php?name=NDReviews&op=Story6&reid=363
the pc shuts down only while gaming or benchmarking....when in logon screen or on desktop with no apps running it does not shut down.
it only happens when there is a blackout
Now I am really confused...With a 1000 VA UPS you might have 1 minute to shut down your PC when running at full load before the battery is dead.... 6 minutes at half load
http://www.newegg.com/Product/Product.aspx?Item=N82E16842102082
So if it only happens "when there is a blackout", how many minutes are you expecting the battery to last with the vastly undersized UPS when you are gaming with a substantial load ?
Your UPS is sized for servicing a 300 watt PSU handing a 250 watt load and that's pushing it... Your GPU alone can pull 200 watts, your CPU 95 watts in gaming. Add 30 for MoBo, 20 for RAM and storage, 20 miscellaneous and you in 365 watt territory. Compensate for PSU efficiency at 87.5% and your UPS is seeing 420 watts.
The general rule of thumb is that your UPS VA rating should be about twice your actual max wattage I use a kil-o-watt meter to measure the wattage being pulled from the wall and multiply by 2 to get the VA rating.
When power goes out, you are on battery and the battery is simply not capable of delivering the wattage you need. If you had a 300 watts PSU pulling about 250 watts from the wall you'd be fine. You have a 650 watter pulling in excess of 420 watts from the wall ... and 850 works theoretically but I'd use a 1000VA unit.
Furthermore, forget about the battery, the circuitry in the UPS may not be capable of handling the load and tripping out. Also did you check your PSU....amd read the link to the UPS article I gave you above ?
http://www.newegg.com/Product/Product.aspx?Item=N82E16817139054
CORSAIR RM Series RM650 650W ATX12V v2.31 and EPS 2.92 80 PLUS GOLD Certified Full Modular Active PFC Power Supply
https://www.dougv.com/2010/03/active-pfc-enabled-psus-are-not-compatable-with-most-low-end-ups/
It turns out that most PC power supply units with active power factor correction (Active PFC) do not work well with lower-cost uninterrupted power supplies (UPS), e.g. battery back-ups....In short, if you send a high-end PSU the current created by a lower-end UPS, the PSU’s built-in power factor correction hates it, and cuts power to the PC immediately. As in, the exact thing you bought the UPS to prevent in the first place is exactly what happens.