I have a customer who has to shut off his main power for 20 minutes every Saturday. Is there a recommended battery backup that will keep one server up and operational for those 20 minutes each week without degrading?
I have a customer who has to shut off his main power for 20 minutes every Saturday. Is there a recommended battery backup that will keep one server up and operational for those 20 minutes each week without degrading?
The APC calculator is a good place to start:
https://www.apc.com/shop/us/en/tools/ups_selector/
https://www.apc.com/tools/ups_selector/pso/zones/
Please answer my question about the degrading part. If I get any backup, is it going to degrade after being drained for 20 minutes every week?
UPS batteries should be changed every 3 to 5 years. Putting a close-to-full discharge on them will probably speed up the replacement time. BUT, a quality UPS will test your batteries every week and tell you if they are starting to degrade. You can then proactively replace them. You want to purchase a UPS that has USB and ethernet interface, IMO. So that you can monitor the performance of the UPS and get alerts.
You can mitigate the degradation over time, by oversizing the UPS. If you only put a 50% discharge on the batteries, they will last longer (with a higher up-front cost) than batteries that you almost exhaust.
You can mitigate the degradation over time, by oversizing the UPS. If you only put a 50% discharge on the batteries, they will last longer (with a higher up-front cost) than batteries that you almost exhaust.
Very true.
And as you noted above, the actual recorded power consumption must be known before spending any money.